Connection troubles in existing installation
#2
Hi splatch,
 
It seems that no one can follow what you mean exactly.
Is the problem already fixed or not?
If not, here are my following steps I would do to find the error:
You need to know which modules are mistaken. For this, take the LCN-Pro with a real coupler without PCHK.  In Busmonitor there has to be something showing what modules are mistaken. After that Cut the data LCN Wire from the modules which are maybe mistaken from the rest of the LCN Bussystem. If the modules are UPP ore Modules with “real” Power Outputs look if they work in the room as “single” Modules without the rest of the system. After that please  look if the rest of the system is working.
It seems if the neutral cable is connected somewhere with the Data wire from LCN. But I think it could be only a module, because the system works a long time as you describe.
It would be also good if you know the firmware of the mistaken modules. Maybe there is a problem which is already known from the hotline of LCN.  I hope the hotline already answers you in an Email and because of this they didn’t answer here. Normal they answer really quick to fix problems like this.
Did you use another system for LCN connection like DOMIQ ?
You can contact me also with an email and we try to fix the problem together.
Greats Sven